Good morning,
Working on a project where we have a electrical room with a MDP which is equipped with several breakers that feeds smaller structures. Originally we had a 200A CB in the MDP feeding a 200A disconnect mounted on the exterior of one of the little structures which fed a 200A panel. Somehow the 200A disconnect forgot to get installed so I suggested that the 200A panel be provided with a MCB but the problem is that the panel is located in the center of the building. Im pretty positive this is compliant because the conductors already have their over current protection in the MDP but just wanted to make sure because the feeder travels a good 20 feet in the building. This seems like it would be confusing for the fire department so I was going to suggest a shunt trip as well.
Working on a project where we have a electrical room with a MDP which is equipped with several breakers that feeds smaller structures. Originally we had a 200A CB in the MDP feeding a 200A disconnect mounted on the exterior of one of the little structures which fed a 200A panel. Somehow the 200A disconnect forgot to get installed so I suggested that the 200A panel be provided with a MCB but the problem is that the panel is located in the center of the building. Im pretty positive this is compliant because the conductors already have their over current protection in the MDP but just wanted to make sure because the feeder travels a good 20 feet in the building. This seems like it would be confusing for the fire department so I was going to suggest a shunt trip as well.