riverstrat
Member
... I don't have a load design, the customer has an existing
3 or 4 KVA irrigation pump on 5 acres.
An old house was removed from the property
last year.
So this is for future expansion convenience so to speak.
One of my older books mentioned sizing one size below given ampacity
indicating I could use 400 mcm cu.
My latter books don't mention under sizing, so it looks like I need to
use 500 mcm cu as per 310-16.
The can will be hung today and a 3" wheatherhead will be installed
in the next few days.
I will be sizing my grd according to my entrance cable so either way
it will probably be 1/0 CU, to an 3/4" 8' grd rod.
Opinions as to the safety advantage of adding a second grd
rod 6' away from the main grd rod would also be apprecitated....