I counted 150 T-5 flourescent lights in my 25,000 square foot facility, plus other lights that I did not count emanating from 3 phase 4 wire lighting panels. Now, I will assume unity power factor and 208/120volts and we all know that each circuit breaker from the 3 phase lighting panel will feed one of its three phases to its respective lights so that the lights in effect are being fed from a single phase off of the 3 phase lighting panel. Assuming 70watts per light, the current yields the following: I=70wattsX150lights/120volts (single phase so it is not necessary to devide by the square root of 3)=87.5amps for a 120volt single phase flourescent lights layout. That is just the lights, not to include a 15RLA air conditioner and a couple of other window air conditioning units, two 20 amp pieces of equipment (one operating at 120volts and the other operating at 480volts), three other 3 amp pieces of equipment, a space heater, 8 computers and some other items.
The electricians measured approximately 30amps on all three phases with 5 amps on the neutral with their ampmeter from the secondary of the set of three 100KVA ground mounted pots, which yields a 3phase, 120/240volt, 300KVA transformer they say is wye-wye connected.
I have a load study which indicates the same amp load for the building also peformed by a consultant.
I would devide the above equation by 277 if the flourescent lights were 277/480volts. Then 70X150/277=38 amps. Still it is not possible to get the 35 amps for the 3 phase reading off all three phases of the transformer secondary with 5 amps on the nuetral. Also, how can there be a nuetral when I only counted 3 wires going in to the building on the aerial service drop entering in to the weatherhead.
How can this be??
As eluded to above the other issue is that both the electricians and the load survey done by a consultant state that it is a wye-wye connection from the transformer when I only counted 3 wires going in to the building from the service drop (meaning there is no ground comming in to the building from the transformer). Wouldn't this have to be a wye-delta configuration.
The electricians measured approximately 30amps on all three phases with 5 amps on the neutral with their ampmeter from the secondary of the set of three 100KVA ground mounted pots, which yields a 3phase, 120/240volt, 300KVA transformer they say is wye-wye connected.
I have a load study which indicates the same amp load for the building also peformed by a consultant.
I would devide the above equation by 277 if the flourescent lights were 277/480volts. Then 70X150/277=38 amps. Still it is not possible to get the 35 amps for the 3 phase reading off all three phases of the transformer secondary with 5 amps on the nuetral. Also, how can there be a nuetral when I only counted 3 wires going in to the building on the aerial service drop entering in to the weatherhead.
How can this be??
As eluded to above the other issue is that both the electricians and the load survey done by a consultant state that it is a wye-wye connection from the transformer when I only counted 3 wires going in to the building from the service drop (meaning there is no ground comming in to the building from the transformer). Wouldn't this have to be a wye-delta configuration.