Service Drop

Status
Not open for further replies.
Yes, I would like to find out what the maximum length and what pervisions should be taken for a service drop in a manufacturing facility using #10-4 S.O . Cord the voltage is 480 volts 3 phase and using a twistlock female connector on the end to plug in equipment.Is there also a standard height off of the floor to the end of the cord from the cieling? If so were can I find it in the NEC. Any input would be greatly appreciated.
 

dcl34769

Senior Member
Location
saint cloud,fl
Re: Service Drop

i could not find a max lenght.

floor height using the cord as the disconnecting means would be no more than 6'7''. if the equipment has a disconnect then you could go above that.
 