Hey guys,
I have a service entrance rated ATS backing up the main switchboard (2000A) and have a separate life safety ATS (400A) for the life safety loads (EM lights). The generator has 2 output breakers feeding these ATS's.
Can a Article 700 (Life Safety) transfer switch be downstream of a Article 702 (Optional STBY) transfer switch?
700.10(B) separation of wiring comes to mind. We will have complete isolation on the emergency side but on the normal side of the LS ATS is fed from the main switchboard, so we will not have isolation.
Also, the downstream LS ATS will always see utility due to the upstream ATS backing up the main switchboard, so it wont ever transfer!