Hello Every One:
I working on a project that has an existing 1200A Main switchboard, 480Y/277V service. The customer wishes to add a generator to backup the entire building. My thinking is as follows:
1. Provide new Service Entrance ATS, 1200A, 4P and locate adjacent to main switchboard.
2. Remove existing service conductors from utility transformer to Main switchboard.
3. Provide new feeder from utility transformer to new ATS and terminate in normal (utility) terminal lugs. The new feeder will utilize existing conduits between the transformer and switchboard but will use the main switchboard as a pulling point to get to the ATS.
4. Remove bonding jumper between neutral and ground bar in switchboard.
5. Pull new feeder from ATS load side back to switchboard.
6. Pull new feeder from generator to ATS emergency terminal side.
Is there any better (cleaner) way on doing this? I just want to make sure I'm not overthinking it. Is there anyway I can use the main switchboard as a service entrance as currently is and still can use an ATS to power the entire building?
Thanks,
I working on a project that has an existing 1200A Main switchboard, 480Y/277V service. The customer wishes to add a generator to backup the entire building. My thinking is as follows:
1. Provide new Service Entrance ATS, 1200A, 4P and locate adjacent to main switchboard.
2. Remove existing service conductors from utility transformer to Main switchboard.
3. Provide new feeder from utility transformer to new ATS and terminate in normal (utility) terminal lugs. The new feeder will utilize existing conduits between the transformer and switchboard but will use the main switchboard as a pulling point to get to the ATS.
4. Remove bonding jumper between neutral and ground bar in switchboard.
5. Pull new feeder from ATS load side back to switchboard.
6. Pull new feeder from generator to ATS emergency terminal side.
Is there any better (cleaner) way on doing this? I just want to make sure I'm not overthinking it. Is there anyway I can use the main switchboard as a service entrance as currently is and still can use an ATS to power the entire building?
Thanks,