Bogiedown170
Member
- Location
- Yonkers, NY, USA
Hi, came across a job last week where a customer had a splice box on outside wall with LFNC (about 5ft) going out straight to generator. Turns out customer wanted the cables buried. An 18” trench was dug and 1” PVC was used to run SE Stye R XHHW-2 (ground was bare) along with control wires (18 AWG 7 Type TC DIR BUR).
I was told that if jacket on XHHW-2 is taken off, it can get buried (Jacket was taken off). As I read the code 338, I’m not finding that SER is okay to bury unless TYPE USE is used. As for the control wire, jacket is rated 600v. Any insight is greatly appreciated. Thanks.
I was told that if jacket on XHHW-2 is taken off, it can get buried (Jacket was taken off). As I read the code 338, I’m not finding that SER is okay to bury unless TYPE USE is used. As for the control wire, jacket is rated 600v. Any insight is greatly appreciated. Thanks.