102 Inspector
Senior Member
- Location
- N/E Indiana
- Occupation
- Inspector- All facets
Currently using 2008 NEC. Table 310.15(B)(6) indicates for a 300 amp service, 250 Awg Copper or 350 Awg Alum is needed. This is a triplex apartment building, but since this Table does not indicate it is for single family, are those conductor sizing correct. In this small town, nobody does load calculations so there would be no further adjustment. Originally I thought 350 Awg Copper or 500 Awg Alum until I remembered Table 310-15. Am I correct in my interpretation for service entrance conductor sizing. Thank you.