I am currently working on an apartment building in southern Indiana. The lead electrician ha figured 2/0 aluminum SER for a 200 amp panel located 30 feet from the meter bank. {i have not done my own calculations as of yet}. I have never seen anything smaller then 4/0 aluminum allowed for a 200 service even when the meter and panel are back to back. I'm just curios if anyone knows of any circumstances where 2/0 AL ser would be allowed for 200 amp service.


please excuse my lack of doing the math before posting
 
I am currently working on an apartment building in southern Indiana. The lead electrician ha figured 2/0 aluminum SER for a 200 amp panel located 30 feet from the meter bank. {i have not done my own calculations as of yet}. I have never seen anything smaller then 4/0 aluminum allowed for a 200 service even when the meter and panel are back to back. I'm just curios if anyone knows of any circumstances where 2/0 AL ser would be allowed for 200 amp service.


please excuse my lack of doing the math before posting

The lead electrician is incorrect or the service size is smaller than 200 amps. Now you can run 2/0 ser to a 200 amp panel as long as it is fused to the appropriate amps.

My guess is he is feeding a sub panel rated 200 amps but will have an ocpd at 125 or 100 amps at the main distribution panel.
 
Table 310.15(B)(6) permits a 4/0 aluminum SER cable that servers and the main power feeder to feed a 200 amp panel.

I suspect that the electrician looked at the copper column of 310.15(B)(6) and saw the 2/0 an missed that that is for copper not aluminum.


Chris
 
Is that panel for one of the apartments? (and the ONLY panel for that apartment?) If so, than you need 4/0 AL per 310.15(B)(6)

If not, than it would depend on the calculated load.

Also, what NEC cycle are you under?

SE cable can be used @ 75? C under the '05 NEC and previous, but you are restricted to the 60? C column under the '08 NEC.
 
Understand rating of SE cable has changed in 2008 code. Table 310.16 60 degree has 4/0 Al rated at 150 amps, but do you still get to use Table 310.15 (B)(6) to rate the cable at 200 amps for 4/0 AL
 
Understand rating of SE cable has changed in 2008 code. Table 310.16 60 degree has 4/0 Al rated at 150 amps, but do you still get to use Table 310.15 (B)(6) to rate the cable at 200 amps for 4/0 AL

Yes but only for dwelling services or feeders that carry the entire load of the service.
 