What type of box store conductors can I use in a 2" conduit to the service head in aliminum? Can URD go into a conduit for service entry 4/0 200a?
Sure, 4/0 aluminum will fit in 2". URD cannot be used in the conduit according to art. 338.12(B). There are some underground use cables that are listed for above ground.What type of box store conductors can I use in a 2" conduit to the service head in aliminum? Can URD go into a conduit for service entry 4/0 200a?
What type insulation are you using for the USE cable.yes residential
URD is not a recognized NEC conductor