Hey everyone,
I have a situation where I have a 250 KW generator at 120/208, 3 phase and it is feeding a service entrance rated 1000 amp transfer switch, which then feeds into a 1000 amp distribution panel. The contractor has sized the feeders at 3 sets of 350 KCMIL copper, which is only good for 930 amps. My question is am I allowed to round up to 1000 amps on my ampacity for my feeders from the generator to the transfer switch or am I pretty much forced to upsize the conductors due to 240.4 in the NEC?
Best Regards
I have a situation where I have a 250 KW generator at 120/208, 3 phase and it is feeding a service entrance rated 1000 amp transfer switch, which then feeds into a 1000 amp distribution panel. The contractor has sized the feeders at 3 sets of 350 KCMIL copper, which is only good for 930 amps. My question is am I allowed to round up to 1000 amps on my ampacity for my feeders from the generator to the transfer switch or am I pretty much forced to upsize the conductors due to 240.4 in the NEC?