hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
I have 1200A CT cabinet that feeds service trough. The trough feeds four separate main service disconnects fused at following: disconnect #1 fused at 400A, disconnect #2 is fused at 400A, disconnect #3 is fused at 400A, disconnect #4 is fused at 600A.
The service entrance conductors in trough is 3 sets of 4#600kcmil which is 1260A. The total overcurrent protection rating of all four service disconnects is 1800A.
The total demand load for the service calculated is 1,198A.
Since the total of all four service disconnects is 1800A and the service entrance conductors is 1260A, inspector flagged it saying total overcurrent protection size of the four service disconnects cannot exceed 1260A since service entrance conductors feeding it are 1260A.
The engineer stated you can and said according to NEC 2017 Article 230.90(A) exception no 3 you are allowed to have total of four service disconnect overcurrent rating exceeding the service entrance conductor amapcity since demand load (1198A) does not exceed service entrance conductor ampacity.
Is the engineer correct or the inspector? Which one?
The service entrance conductors in trough is 3 sets of 4#600kcmil which is 1260A. The total overcurrent protection rating of all four service disconnects is 1800A.
The total demand load for the service calculated is 1,198A.
Since the total of all four service disconnects is 1800A and the service entrance conductors is 1260A, inspector flagged it saying total overcurrent protection size of the four service disconnects cannot exceed 1260A since service entrance conductors feeding it are 1260A.
The engineer stated you can and said according to NEC 2017 Article 230.90(A) exception no 3 you are allowed to have total of four service disconnect overcurrent rating exceeding the service entrance conductor amapcity since demand load (1198A) does not exceed service entrance conductor ampacity.
Is the engineer correct or the inspector? Which one?