I am increasing the service to an industrial machine shop building that includes HPS lighting, a small office space (875 sg ft) and warehouse space (30,000sq ft). The existing service is 400amp 277/480volts. The new service will be 1000amps 277/480volts. On the line side of the utility CT metering cabinet I plan to install 3 parrallel sets of 400MCM THHN/THWN CU conductors in 3 inch schedule 80 PVC. 310-16 shows the 400 as rated for 335amps at 75 deg rating. The majority of the load in this building is 3 wire motor loads. I am not reducing the neutral and am not including it as a current carrying conductor. (FYI)On the load side of the CT cabinet will be 2 panelboards. One will be the existing 400 amp panel that already includes a 400 amp service disconnect breaker. The second will be a new 600 amp panelboard with a 600 service disconnect breaker. With regards to the line side conductors - do you agree with my use of 400MCM?