hhsting
Senior Member
- Location
- Glen bunie, md, us
- Occupation
- Junior plan reviewer
Attached sketch shows two sets of service entrance conductors in building with one tenant occupancy. Sketch shows power riser and elevation view. One set of service entrance conductors feed second floor Panel P2 with meter inside building and second set of service entrance conductors feed first floor Panel P1 with meter inside building. Panels P1 and P2 have main breaker but they are not grouped. Both floors belong to one tenant one occupancy.
The building is commericial assembly location.
I would guess skerch is not complaint per NEC 2014 Article 230.4 first paragraph. I am confused by 230.4 exception number 2 which says supply separate loads which to me indicates more than one occupancy.
Anyways my question: which of the following ways would make installation complaint with NEC 2014 Article 230.4 or its exceptions:
1. Have two sets of service entrance conductors in building but group Panels P1 and P2 together. If this makes it code complaint then which exception 230.4.
2. Provide two service disconnects one at each of the SRVC Entrance conductors outside over trough and group them. If this makes it code complaint then which exception 230.4.
3. Provide one service entrance conducfor and combine Panels P1 and P2 to one panelboard with main breaker per NEC 2014 Article 230.4
4. Any other ways this could become NEC 2014 Article 230.4 or its exceptions code compliant.
Than kyou for your input
The building is commericial assembly location.
I would guess skerch is not complaint per NEC 2014 Article 230.4 first paragraph. I am confused by 230.4 exception number 2 which says supply separate loads which to me indicates more than one occupancy.
Anyways my question: which of the following ways would make installation complaint with NEC 2014 Article 230.4 or its exceptions:
1. Have two sets of service entrance conductors in building but group Panels P1 and P2 together. If this makes it code complaint then which exception 230.4.
2. Provide two service disconnects one at each of the SRVC Entrance conductors outside over trough and group them. If this makes it code complaint then which exception 230.4.
3. Provide one service entrance conducfor and combine Panels P1 and P2 to one panelboard with main breaker per NEC 2014 Article 230.4
4. Any other ways this could become NEC 2014 Article 230.4 or its exceptions code compliant.
Than kyou for your input