Service entrance conductor

Status
Not open for further replies.

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I have two sets of 350 kcmil incoming service entrance conductor to service disco. GEC size based on 350 kcmil which is 1/0 AWG CU or based on 350x2 = 700 kcmil which is 2/0AWG CU?

All reference based on NEC 2014. Thanks for input
 

Carlos Murillo

New User
Location
NJ
Occupation
engenier
Greetings, I would like to consult: if I apply the temperature adjustment factors and number of conductors, based on 310.16 at 90 ° C, but the terminals of the device are for 75 ° C. So I have to choose 310.16 at 75 ° C?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
You may calculate using the 90 deg rating, but your final result does not allow you to exceed the 75 deg rating.
 