Here is the scenario. I have a 480v 1200 amp service. Service conductors come from pad mount transformer and go to a ct cabinet. From the ct cabinet the service entrance conductors go into a 3'' ridgid pipe to the switch gear. Had an inspection today and forgot to install grounding bushings on the pipe and instead used just a pvc bushing and it passed. I was always under the impression that you had to install grounding bushings on raceways for service entrance conductors. I looked at 250.80 and 250.92 and still believe i am correct. Am i missing something because of the ridgid pipe or did the inspector just miss something?