My question is this,Im looking at a job that has a 320a meter base on the side of a metal garage. Out of the meter base there is a 200a feed going to a QO panel with a main breaker about 10 feet away inside the garage.The 200a feed is coming off of 1 set of the double barrel lugs.I dont have a problem with this because the tap rule should cover this. The problem is,the owner wants to run a 200a feed to his new house which is about 200 feet away directly off of the double barrel lugs with no OCP until he hits the the main in his new house. IMO,the new SEC's would not be covered by a tap rule and would be a violation. In my mind I am thinking a 200a fused disconnect or a set of fuses off to the side of the meter base would satisfy the requirements. I have strolled thru Article 230 and cannot find any other way this could be done. The owner is wanting a bid from me and I would like the job,but I am afaid my competition will look past this.This is in a rural environment so there isnt a AHJ to discuss it with.Any thoughts?