I would like to identify a listed product that is suitable for splicing a (2)350kcml and 3/0AWG service conductor within the gutter spacing inside a 600A rated panelboard before termination into the main service equipment (Circuit Breaker) disconnect.

The (2)350kcml is the utility service lateral conductor and the 3/0AWG is from a exterior mounted PV system feeding back into the grid.

The problem is that the CB terminations will only accept a maximum of 2-sets of service conductors and that we want to identify a clean/neat installation method to splice in the third conductor.

Thanks,

[ April 08, 2004, 05:51 PM: Message edited by: mp101 ]
 
Re: Service Entrance Conductors Splice

Compression spices and heat shrink would be one method. Take a look at section "
230.33 Spliced Conductors.
Service-lateral conductors shall be permitted to be spliced or tapped in accordance with 110.14, 300.5(E), 300.13, and 300.15."
 