service entrance conductors

Status
Not open for further replies.

eza

Member
What is the distance, if any, do service entrance conductors coming out of service panel to meter base have to be before requiring a disconnect, if any disconnect at all because the feeders are not passing through home. I can't find any code reference to this, see picture, thanks to all.
 

Attachments

  • CAM00633.jpg
    CAM00633.jpg
    132.5 KB · Views: 0

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
SEC's on the outside of the structure have no length limitation. 230.70(A)(1) is one code reference for entrance into the structure.
 