I have a project that has an overhead service coming down to the PoCo meter and then into a 100 amp disconnect. Out of the disc I have 2-2-2 and a #6 aluminum going to a 100 amp breaker panel. The conductors of the 2-2-2 have on the insulation "Type USE-2 or RHH or RHW-2". I got a call from the inspector saying that I couldn't use USE going into the building because NEC 338.12 (B) says Uses Not Permitted (1) For interior wiring and not (2) for aboveground installations except where USE emerges from the ground and is terminated in an enclosure at an outdoor location and the cable is protected in accordance with 300.5(D).
I understand that USE is not permitted in this application BUT this is Type USE-2 or RHH or RHW-2. Ok, so.....Under the definitions of 338.2 an SE cable has a flame-retardant moisture resistant covering. USE has a moisture resistant covering but not required to have a flame retardant covering. In the insulation tables in NEC 310.104 the table for USE and USE-2 say moisture resistant covering and heat resistant covering. It also says if more than one conductor in the cable refer to 338. The tables for RHH and RHW-2 say flame retardant and moisture resistant covering. Since the conductors have multiple insulation types and characteristics and from what I can see there's nothing prohibiting RHH or RHW-2 from being installed in a conduit entering a building to feed a panel.......wouldn't the cable that's installed work? I'm assuming the USE can't be used because it lacks the flame retardant feature but since the cable is also rated as other types of insulation that do have a flame retardant feature I think it should be able to be used.
So...what's the answer? One says you can't but the other two types say you can or at least don't say you can't.....?
I understand that USE is not permitted in this application BUT this is Type USE-2 or RHH or RHW-2. Ok, so.....Under the definitions of 338.2 an SE cable has a flame-retardant moisture resistant covering. USE has a moisture resistant covering but not required to have a flame retardant covering. In the insulation tables in NEC 310.104 the table for USE and USE-2 say moisture resistant covering and heat resistant covering. It also says if more than one conductor in the cable refer to 338. The tables for RHH and RHW-2 say flame retardant and moisture resistant covering. Since the conductors have multiple insulation types and characteristics and from what I can see there's nothing prohibiting RHH or RHW-2 from being installed in a conduit entering a building to feed a panel.......wouldn't the cable that's installed work? I'm assuming the USE can't be used because it lacks the flame retardant feature but since the cable is also rated as other types of insulation that do have a flame retardant feature I think it should be able to be used.
So...what's the answer? One says you can't but the other two types say you can or at least don't say you can't.....?