Hi ,
I am working on a multi family building and I just fail the inspection.
I have two meter stacks . One two meter stack 200A and the other one is a three meter stack 300A .I install on the top of them a trough and from the trough I was running 4in rigid to the overhead.
The inspector is telling me that I am not allowed to have two sets of service entrance conductors in the same conduit.
There are no splices in the trough each set of cables are going to separate enclosure.4/0 aluminium to 200A meter stack and 350 mcm to the 300A meter stack. They are telling me that I am running conductors in parallel but is not.
The cables are ending in different enclosures.
What do you think what I am doing wrong?
Thank you,
Marius Galetus