Service-Entrance Conductors

Status
Not open for further replies.

Karl H

Senior Member
Location
San Diego,CA
Does anyone know where in the code book ,that states ,it is permitted
to use THHN or THW for Overhead Service-Drop conductors? Since 310.13
does not list THHN or THW as "Sunlight Resistant." Per 310.8 (D).Am I
overlooking something here?
 
Karl H said:
Does anyone know where in the code book ,that states ,it is permitted
to use THHN or THW for Overhead Service-Drop conductors? Since 310.13
does not list THHN or THW as "Sunlight Resistant." Per 310.8 (D).Am I
overlooking something here?



the southwire THHN I use says "Sunlight resistant" right on the wire itself. It has always passed with inspectors.

~Matt
 
I don't do many "Over-Heads" here. I have done many in the past and I've
never even thought about it until tonight. I guess I have too much time on
my hands. lol
 
Karl H said:
Does anyone know where in the code book ,that states ,it is permitted
to use THHN or THW for Overhead Service-Drop conductors? Since 310.13
does not list THHN or THW as "Sunlight Resistant." Per 310.8 (D).Am I
overlooking something here?
Are ANY conductors listed as "Sunlight Resistant" in T310.13?
[Hint: 310.11(d)]


310.8(D) allows the cables listing - among other choices - to accomplish the requirement of 300.6(c)(1).
Here is one such example of the listing proerties: http://www.southwire.com/ProductCatalog/proddetail.jsp?htmlpreview=true&token=1&desc=CU-THHN

(All references to 2005 NEC)
 