The electrician term for this is "unfused service entrance conductors". The overcurrent protection is on the primary side of the POCO transformer.
The definition of overcurrent says "it may result from overload, short circuits or ground faults". Service conductors are only protected from overloads, as you have done a load calculation on the service. There is no protection against short circuits and ground faults except by the POCO fuse on the primary.
There are three parts to the protection of unfused conductors
1. Additional bonding
2. Restriction on the type of raceway allowed
3. Distance the raceway can go in a building
In Washington we can't use SE cable or EMT, and the distance is limited to 15 ft of raceway, by state rules. Some pocos may require Sch 80 PVC.
once you are past the service, you are using the rules for feeders or branch circuits and since you have short circuit and ground fault protection, additional bonding is typically not required (but are for 480V and hazardous locations)