I am an instructor for the IBEW. Myself, and my fellow colleagues have been discussing this issue for quite some time. here's the question 230.42(B)states that "the minimum ampacity of ungrounded conductors for specific installations shall not be less than the rating of the service disconnecting means". Does that throw out the window the option provided by 240.4(B)that basically one could use a 500Kcmil copper conductor rated 75 degrees C with an ampacity of 380A, and protect them with a 400A breaker. A couple of us say you must use 600Kcmil for service entrance, and the others here believe 500Kcmil is adequate. Any help or opinions?