Service entrance disc.

Status
Not open for further replies.

geochurchi

Senior Member
Location
Concord,NH
Occupation
Retired electrician
Hi,I am required to have a disconnect at the meter socket,do I need a disconnect in the panel located directly behind the meter?
Thanks
 
Hi,I am required to have a disconnect at the meter socket,do I need a disconnect in the panel located directly behind the meter?
Thanks
You need a service disconnect either in the panel behind the meter or one next to the meter, but not both. Be aware though that some POCO's require the main to be adjacent to the meter and some AHJ's don't allow service conductors to enter the building-so you may need to put it outside next to the meter, even though it is not required to be by the NEC.
 
Service entrance disc

Service entrance disc

The utilities in NH require a disco at the meter most are using a combo meter and disco.
 