service entrance disconnect means

Status
Not open for further replies.

rv3152

Member
at the point of entry of service conductor can a disconnect be used and then go from disconnect to main in panel
 

ron

Senior Member
Re: service entrance disconnect means

Yes. The disconnect will have to be rated as "suitable for service entry". The n-g bond would occur either at the meter or first disconnect. The main in the panelboard will not be required, although you could leave it to give a convienient local disconnect.
 