J jnh Member Oct 27, 2004 #1 Does the NEC require the servcice entrance grounded condcutors to be run in the same raceway (conduit) or can it be in a separate raceway (conduit) that is adjacent to the raceway containing the phase conductors?
Does the NEC require the servcice entrance grounded condcutors to be run in the same raceway (conduit) or can it be in a separate raceway (conduit) that is adjacent to the raceway containing the phase conductors?
B bphgravity Senior Member Location Florida Oct 27, 2004 #2 Re: Service Entrance Ground in same raceway They should all be in the same raceway. See section 300.3(B) of the NEC 2002.
Re: Service Entrance Ground in same raceway They should all be in the same raceway. See section 300.3(B) of the NEC 2002.