J jnh Member Oct 27, 2004 #1 Does the NEC allow the copper tape shield on medium voltage shielded cable to be used as the service entrance grounded conductor or equipment grounding conductor for feeders?
Does the NEC allow the copper tape shield on medium voltage shielded cable to be used as the service entrance grounded conductor or equipment grounding conductor for feeders?
B bphgravity Senior Member Location Florida Oct 27, 2004 #2 Re: Service Entrance Grounded Conductors and Equipment Groun I say no to both. I do not know how you would be able to determine the current-carrying capability and Section 250.118 does not list it as an acceptable type of EGC.
Re: Service Entrance Grounded Conductors and Equipment Groun I say no to both. I do not know how you would be able to determine the current-carrying capability and Section 250.118 does not list it as an acceptable type of EGC.
B bwilson Member Oct 27, 2004 #3 Re: Service Entrance Grounded Conductors and Equipment Groun Take a look at part X of Art. 250. Start with 250.184
Re: Service Entrance Grounded Conductors and Equipment Groun Take a look at part X of Art. 250. Start with 250.184