Does the NEC allow the copper tape shield on medium voltage shielded cable to be used as the service entrance grounded conductor or equipment grounding conductor for feeders?
 
Re: Service Entrance Grounded Conductors and Equipment Groun

I say no to both.

I do not know how you would be able to determine the current-carrying capability and Section 250.118 does not list it as an acceptable type of EGC.
 
Re: Service Entrance Grounded Conductors and Equipment Groun

Take a look at part X of Art. 250. Start with 250.184
 