102 Inspector
Senior Member
- Location
- N/E Indiana
- Occupation
- Inspector- All facets
I have never seen this before and question application. "Electrician" installed meter base, new service conductor from weatherhead to line side, 3 wire. From load side of meter, a 4 wire cable was run to a load center. The grounded conductor and grounding electrode were bonded inside the meter base. A grounding lug was screwed to the meter base and then connected to 2-ground rods via a #4 bare copper conductor. I refused the installation based on 250.24(A)(1) and 250.8 of the 2008 NEC. Could this even be considered acceptable?