New member
I am trying to determine if a main device is needed on the service entrance equipment. The site is serviced by an outdoor, utility-owned 1000 KVA transformer, 13.8 kV x 480/277V, where the secondary conductors are routed directly into the building. The distance from the transformer to the point of entrance well exceeds 25 ft. The service entrance equipment will be located immediately inside the building at the nearest point of entrance and will be owned by the Customer. Article 230.90 does not require a main overcurrent protection device as part of the service entrance equipment and makes no reference to a distance limitation from the transformer secondary to the service disconnect. However, Article 240.21 does require the use of a main device and, in this sense, conflicts with the information stated in Article 230.90. Since none of the exceptions in 240.21 (i.e. A thru G) apply to my situation, I assume that a main is required. Does Article 240.21 apply to my situation and why does it conflict with Article 230.90?