Follow up question on a post from a couple months ago. There's no real reason to read through the link, but I figured I will reference it in case someone recognizes the language. http://forums.mikeholt.com/showthread.php?t=191611&highlight=
I have a new question, here is a summary (with updated information):
I have an install going in with a 480V exterior pad-mount delta:wye utility transformer feeding an adjacent connection cabinet. The connection cabinet has no overcurrent protection (which is typical for utility installs in our area). The cabinet will feed some chillers (which have service rated disconnects at them) and also will feed a 480:208V 500kVA delta:wye step down transformer which in turn feeds the building. We added a service entrance rated disconnect ahead of the transformer.
A few questions:
1. Does this installation require a neutral from utility transformer to the primary SE disconnect in front of the stepdown transformer? If so does it need to be full size? It's a weird situation in two ways - (1) we're feeding a transformer more or less straight from a transformer; and (2) in there being a ~service entrance~ disconnect protecting the 2nd transformer. I had a grounding electrode conductor specified from utility to stepdown, but not any neutral. Transformers don't generally require a neutral to them, but does the SE disconnect require one? I'm confused as to what principles take precedence here.
2. Do the chillers also require neutrals from utility xfmr to their SE disconnects? The chillers were specified with grounding electrode conductors but no neutrals.
Thanks in advance!
I have a new question, here is a summary (with updated information):
I have an install going in with a 480V exterior pad-mount delta:wye utility transformer feeding an adjacent connection cabinet. The connection cabinet has no overcurrent protection (which is typical for utility installs in our area). The cabinet will feed some chillers (which have service rated disconnects at them) and also will feed a 480:208V 500kVA delta:wye step down transformer which in turn feeds the building. We added a service entrance rated disconnect ahead of the transformer.
A few questions:
1. Does this installation require a neutral from utility transformer to the primary SE disconnect in front of the stepdown transformer? If so does it need to be full size? It's a weird situation in two ways - (1) we're feeding a transformer more or less straight from a transformer; and (2) in there being a ~service entrance~ disconnect protecting the 2nd transformer. I had a grounding electrode conductor specified from utility to stepdown, but not any neutral. Transformers don't generally require a neutral to them, but does the SE disconnect require one? I'm confused as to what principles take precedence here.
2. Do the chillers also require neutrals from utility xfmr to their SE disconnects? The chillers were specified with grounding electrode conductors but no neutrals.
Thanks in advance!