Pat Bass
Member
- Location
- San Antonio, TX
We have a disagreement among the Engineering Staff (as you would expect).
The scenerio is this. Pole mounted service transformer (fused on high side)
with a fused disconnect switch at the bottom of the pole. (service is not metered since it is our own power). Inside the fused disconnect switch the service transformer neutral, the Grounding Electrode Conductor, the Equipment Ground Conductor and the Neutral conductor to the panelboard are bonded to the case and the Grounding Electrode Conductor goes to the Grounding Electrode.
The disagreement is this. The wires from this point to the panelboard (or in some cases an Automatic Transfer Switch) it is feeding are by some refered to as Service Entrance Conductors, by some as Service Laterals. I say they are Feeders. Who is correct? They are underground and in some cases run 100' or more.
The scenerio is this. Pole mounted service transformer (fused on high side)
with a fused disconnect switch at the bottom of the pole. (service is not metered since it is our own power). Inside the fused disconnect switch the service transformer neutral, the Grounding Electrode Conductor, the Equipment Ground Conductor and the Neutral conductor to the panelboard are bonded to the case and the Grounding Electrode Conductor goes to the Grounding Electrode.
The disagreement is this. The wires from this point to the panelboard (or in some cases an Automatic Transfer Switch) it is feeding are by some refered to as Service Entrance Conductors, by some as Service Laterals. I say they are Feeders. Who is correct? They are underground and in some cases run 100' or more.