Service Entrance Rated 4-Pole ATS & Neutral / Ground Bonding Code Violation?

Merry Christmas

JediMike

Member
Location
New England
We have a project where we designed a generator and service entrance ATS for a commercial building. Due to supply issues, the EC can only get a 4-pole SER ATS (with 1000A, 120/208V, 3P main circuit breaker). So that would create a separately derived system, requiring the generator to have a neutral to ground bonding jumper. My question is, does this create a code violation because the SER ATS also has a neutral to ground bonding jumper, or does switching the neutral break that bonding?
 

JediMike

Member
Location
New England
Augie, that was actually my suggestion as well, but done by the vendor/manufacturer and not the EC. He is looking into it with them, and I am sure they can do it. But if they can't, it goes back to my original question.
 

qcroanoke

Sometimes I don't know if I'm the boxer or the bag
Location
Roanoke, VA.
Occupation
Sorta retired........
With a switched neutral you need to bond neutral to ground at both sources.
I would not do this in the ATS. Bond in the generator and at the service disconnect.
Also is GFI protection required for 1000 amps @ 120/208?
 