Am I wrong that for an Automatic Transfer Switch to be Service Entrance Rated it is to have an OCPD located in it and some means of manual disconnect?
Please correct my below conductor classifications as needed:
Service Entrance Conductors - From the Meter to the ATS
Feeder - From the Load Side of the Service Entrance Rated ATS to the Indoor Panel with MCB.
Feeder - From the Generator Circuit Breaker to the ATS.
Assuming the above is correct then is it fair to say that conductors between the ATS and panel being supplied in a building can not be considered underground service conductors (assuming they are underground) and thus have an ampacity of only 100% of the load NEC 230.31 (A)?