Service Entrance Rated ATS

Status
Not open for further replies.

Npstewart

Senior Member
Hi Everyone. I have a pretty easy question.

We are adding a generator (100kw) to a existing 400A service. Currently, the 400A service has a fused disconnect for the building prior to feeding panels inside. The transfer switch and generator was already purchased in a package deal prior to us getting involved. Originally I was going to the ATS from the generator and transformer, then I was feeding the existing disconnect which then re-fed the existing panels. I was then informed that the ATS was not service entrance rated. Now I am thinking that I need to go into the 400A disconnect FIRST, then feed the ATS, then re-reed the panels. The only problem is, when someone throws the 400A disconnect it will start the generator, then they will have to walk to the generator to flip the breaker. Am I over thinking this? Im getting over the flu so not thinking clearly right now.
 
I think your assessment is correct.

As far as the generator starting when the main disconnect is thrown, you can look into installing an electrical interlock switch in the main disconnect to prevent the generator from starting when the disconnect is opened.
 
I think your assessment is correct.

As far as the generator starting when the main disconnect is thrown, you can look into installing an electrical interlock switch in the main disconnect to prevent the generator from starting when the disconnect is opened.
I agree.
 