I told the inspector that the disconnect can be locked out and this is his response.
The installation is deemed, as is, to be a danger to the general public, particularly children, in that it is exposed to the general public. Please provide an installation that complies with the following sections of the 2017 edition of the National Electric Code:
- 110.26 (E)(2)(a)(2) requires protection from accidental contact by unauthorized persons.
- 230.70( c). The service panel installed is not suitable for the prevailing conditions. i.e., without an enclosure with a dead front panel, the electrical equipment is accessible to unauthorized persons, with particular emphasis to children.
- 100. A dead front “without live parts exposed to a person on the operating side of the equipment” is required.
- 408.38. Required to have a dead front for protection of the general public (not be accessible to unqualified persons).
Providing an installation that is compliant with the above is required. Please notify me when corrections are completed, for re-inspection.