We are in the process of wiring a retail building
Electrical inspector failed the electrical service on these grounds
338-4a
336-26
We are using type 4/0 SER cable which is rated 90 degree. For meter stack to main lug panel
He states that we should be in the 60 degree column which would be 150amp
I believe it should be 180amps(75 degree)on a 200amp circuit breaker
All equipment is rated for 75 degree & confirmed with the manufacturer.
Am I wrong?