in a residential application, is emt allowable from the LB to the electric panel inside the residence, everything on the outsidefrom the load side of the meter to the LB is Rigid, as is the riser?
And of course make sure that you use the right fittings to attach your EMT to the LB.
Shhh! Don't open that can of worms:happysad:LOL. And just how does one connect EMT to an LB in a manner consistent with the listing?
and also don't forget you will be parrelling the neutral from the meter to the first disconnect. I still ponder that. I did a 400 a (320) ans used all ridged conduit. Inspector had no issue neither did utility.
Not quite sure what you're talking about here. OP didn't mention using parallel conductors, or any conductors as far as that goes.:?
and also don't forget you will be parrelling the neutral from the meter to the first disconnect. I still ponder that. I did a 400 a (320) ans used all ridged conduit. Inspector had no issue neither did utility.
Not quite sure what you're talking about here. OP didn't mention using parallel conductors, or any conductors as far as that goes.:?
LOL. And just how does one connect EMT to an LB in a manner consistent with the listing?
"Unobjectionable" violation might be a more fitting term.Been discussed previously. As I recall it is looked upon as a "accepted" violation of 250.6.
in a residential application, is emt allowable from the LB to the electric panel inside the residence, everything on the outsidefrom the load side of the meter to the LB is Rigid, as is the riser?
LOL. And just how does one connect EMT to an LB in a manner consistent with the listing?
Service conductors are allowed to be protected by EMT. Sounds like a shirt pocket rule or a local way of doing things.No what i ment is that I installed a 150amp single phase service in 1 1/2 conduit condiut 2/0 wire rigid on the outside and where i entered the house, I converted to EMT. It got tagged the inspector said that they are unprotected service conductors and that I needed to have rigid all the way to the panel. I had never heard of this before. 20+yrs Located in northern Illinois
Do they make any that are rain tight when used with EMT? I'm guessing those are not.Use the correct LB?
One that takes both EMT and Conduit.
Do they make any that are rain tight when used with EMT? I'm guessing those are not.