service entrance

Status
Not open for further replies.

orr30

Member
I have a question.....my dads house was built in the early 70's and the service entrance wire is an old cloth type with 2 conductors and bare stranded neutral.it is exposed with no conduit.the outer jacket has deteriorated and the bare neutral is exposed throughout the run.the two hot wires still has their cloth jacket on them.how safe is this???????i told my dad that he needs to call the power company and have them come change it.with the bare neutral showing,isn't that a shock hazard??????just wanted to double check before he called them... thanks for any replies.......
 

charlie

Senior Member
Location
Indianapolis
Re: service entrance

The cable you are discussing is old SE cable. The outer jacket should be in tact but the responsibility is the home owner, not the electric utility. Please contact an electrical contractor to replace your dad's service entrance cable, this could be dangerous. :D
 

charlie b

Moderator
Staff member
Location
Lockport, IL
Occupation
Semi-Retired Electrical Engineer
Re: service entrance

Originally posted by zmikc115: Does anyone know what Charlie's rules are? I have never heard of them. Just curious.
This question is beyond the context of the original topic. But I'll answer it, somewhat briefly.

Calling them "Charlie's Rules" is giving them more than their due. But I am the "Charlie" who wrote them, not "Charlie E." There is nothing formal. It's just a few observations that I have made over the centuries. One of them can be found here.
 

apauling

Senior Member
Re: service entrance

if this is a service drop, the line from the power co. to the house, this is common practice. It is not the homeowner's responsibility. it is the poco's. However, if this is the conductor that runs from the meter to the interior, or main breaker to the interior, then it is not up to current code. that still may not be such an alarming hazard.

paul
 

orr30

Member
Re: service entrance

this is coming from the service drop down to the meter.it seems to me this would be the poco's responsibility and not the homeowner.from the meter to the inside panel would be the homeowners,or does it vary from different locations?thanks for all the info....
 

charlie

Senior Member
Location
Indianapolis
Re: service entrance

OK, I am surprised. We install the service drop, make the connections from the service drop to the service entrance conductors, and set and seal the meter. Everything else is the customer's responsibility.

I highly recommend you contact the serving electric utility to find out what their rules are. :D
 

hurk27

Senior Member
Re: service entrance

Yep Charlie there are area's that wont let us laymen even do any connections all the way to the main breakers/disconnect :( (not in this area though) I guess they don't trust us with unprotected wires? :roll:
 

rrrusty

Senior Member
Location
Colorado
Re: service entrance

For some POCO's, the customer is responsible from the weatherhead down and it is not an uncommon practice to install SEU cable that is secured to the side of the structure from the weatherhead to the meter; I have seen a lot of this in the northeast
 

hardworkingstiff

Senior Member
Location
Wilmington, NC
Re: service entrance

Originally posted by rrrusty:
For some POCO's, the customer is responsible from the weatherhead down and it is not an uncommon practice to install SEU cable that is secured to the side of the structure from the weatherhead to the meter; I have seen a lot of this in the northeast
We did it all the time in the Va. Beach area back in the 70's
 

megawatt

Member
Location
Central Kentucky
Re: service entrance

The biggest problem I've seen this situation cause, is water getting into the service entrance cable, running down between the two phase conductors directly onto the neutral connection in the meter base rust & corrosion then cause a bad neutral connection,more often than not, damage electrical appliances, & electronics inside the home.
It's not a question of IF this will happen but WHEN.
The sad thing I often see is a Customer who has to pay to bring their service up to code, & also replace that big screen TV because They didn't act sooner.
This needs to be upgraded as soon as possible.
Good Luck to You !!
 

satcom

Senior Member
Re: service entrance

megawatt,
You are right ,should be replaced ASAP, the water may enter, and cause multiple problems, we see this all the time, and the damage it does.
 