I have install on plans which have SE cables from utility meter to main service fused disconnect outside without conduit. The main service fused disconnect and meter are attached to wall outside.

When asked to provide conduit for SE rated cable between utility meter and main service disconnect the designer took of the SE rated cable and said it would be just be regular cable in conduit. Does the service entrance cable have to be SE cable or it can be any regular cable inside conduit?
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
If they're service entrance conductors they have to comply with a wiring method in 230.43.
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
Those individual conductors (they're not a cable) in a RMC raceway would be code compliant.
 