Bill W said:Sounds like that meter has a 100A and 200A breaker in the meter panel, so that's your bonding point, and not in the panels.
iwire said:I did not see any mention of a 'meter panel'.
I see this as simply a two gang meter socket supplying two main breaker panels.
If I am correct in that assumption I agree with Trevor, both panels will need to be bonded.
Jim W in Tampa said:Maybe i am reading it wrong but he said THE METER so i am thinking only one meter but 2 panels.In that case i would say bond at both panels.
77401 said:I agree with Trevor
This is a typical install down south for a larger residence.
Not trying to read anything into the OP but 200 amp Meter outside into a gutter. Directly inside are the 2 Main breaker panels. Bond each panel, echa panel has a seperate EGC to the Ground rod
Jim W in Tampa said:Here the poco would want the ground rod/rods to go to the meter.Grounds rods to each panel would cause a parallel nuetral
That's close to correct, but a single ground rod is only a supplemental ground. (Gotta stop leaving my code book at work!) A single ground rod must be supplemeted by another ground rod at least six feet away unless you also have 10' or more of underground metal water pipe, ufer ground, building steel, (not in that order of preference.) Does you local utility also require grounding of the meter socket? Here they do. The utility sees that as a piece of equipment, and they want it grounded.tech25 said:So Iam I correct in saying you bond both pannels and have a common ground rod. If you have a disconnect before the pannels you ground the neutral there?
Bill W said:Does you local utility also require grounding of the meter socket? Here they do.
That is shocking! BTW...love your avatar. Looks like he was standing in water when he grabbed that ungrounded conductor.77401 said:This might come to a shock to those of you that are up north. But down here the water meter is out front 10' away from the curb burried about a foot in a plastic box.
So to answer you Q.....Nope
It amazes me that we as electricians are required to follow the NEC but the pocos have individual requirements.Here as jim stated we attach the ground wire inside the meter can.Thats it inside only,but go elsewhere it is ok to do it within the panel.The pocos have no inspection here ,for the most part they sub the work out and that is not inspected(scary huh).But the internal wiring of a home is scrutinized .The pocos should IMHO have to be inspected just like the EC`s work has to be.bikeindy said:Here you better keep that grounding conductor away from that meter or you will never get hooked up.
tech25 said:So Iam I correct in saying you bond both pannels and have a common ground rod. If you have a disconnect before the pannels you ground the neutral there?