each building will be 6 two story townhouses...by bad design and tight spacing the POCO will come underground to 6 200 amp meters..(3 meters on the right side end unit and 3 on the left)...from each meter will we will run underground in a "bundled" 4/0 AL URD, (3 wires commonly called "sweetbriar") to a 200 amp panel in the garage....is this wire rated for this application ie going directly into the panel....
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
If it is truly URD then I would say it is not code compliant however there are some that are underground cables that have a dual rating. My supply company stocks only dual rated underground quad cable.. Look at 338.12(B)
 