Service equipment barriers for backed main breakers

Merry Christmas

darekelec

Senior Member
Location
nyc
I found only square d manufacturing barriers for their backed main breakers . How do you protect breaker terminals in other manufacturer’s panels?



230.62(C) Barriers. Barriers shall be placed in service equipment such that no uninsulated, ungrounded service busbar or service terminal is exposed to inadvertent contact by persons or maintenance equipment while servicing load terminations.
 

Attachments

  • IMG_4313.jpeg
    IMG_4313.jpeg
    70.9 KB · Views: 1
It’s common around here to provide 100 amp backed breaker for plp panel, store or other panels that have a service conductors going to backfed breaker
 
What is a PLP panel?

Since almost all loadcenters manufactured today are main lug/main breaker convertible I think the manufactures want yo to use the main breakers they offer for the loadcenter.
 