I was wondering if I was interrupting section 230.71 correctly.
There are 3 tenants in the building sharing the same electrical service (Tenant #1, Tenant #2 and Landlord)
But there is no main service disconnect on the MDP to the incoming electrical service of 1600 AMPS but I do count a total of 7 Disconnect and 4 MLO Panels.
The Landlord wants to connect a new Panel to the distribution service to service a new elevator.
I feel like the only way this is possible is to install a new Service Disconnect for the 1600 AMP service since there is more than 6 disconnect. (There is a total of 7 Disconnect)
What are my options to install a new 200 AMP panel for the Landlord to install a new elevator.
Please refer to riser diagram for your reference.
Note: There are currently 3 meters (1 meter from utility company. The two other meters are submeters)
View attachment 2563171
There are 3 tenants in the building sharing the same electrical service (Tenant #1, Tenant #2 and Landlord)
But there is no main service disconnect on the MDP to the incoming electrical service of 1600 AMPS but I do count a total of 7 Disconnect and 4 MLO Panels.
The Landlord wants to connect a new Panel to the distribution service to service a new elevator.
I feel like the only way this is possible is to install a new Service Disconnect for the 1600 AMP service since there is more than 6 disconnect. (There is a total of 7 Disconnect)
What are my options to install a new 200 AMP panel for the Landlord to install a new elevator.
Please refer to riser diagram for your reference.
Note: There are currently 3 meters (1 meter from utility company. The two other meters are submeters)