jimingram
Member
- Location
- St Paul MN
On a service call to repair the boiler circuit I became aware the steel enclosures of the service equipment, meter bank, and house panel were energized. The grounding electrode conductor has 38 amps flowing over it to the incoming cold water pipe. The boiler circuit conductors had burned because the conduit and jbox had overheated due to current flow over them.
It is an apartment building part of a multibuilding complex. It was built in the late sixties, early seventys. The 400 amp, 1 phase, service entrance conductors are in two parallel PVC conduits. They are not properly wired. There are two neutrals and two ungrounded conductors (same phase) in one conduit. There are two ungrounded conductors (same phase), no neutral, in the other conduit.
The conductors land on individual lugs. There is no problem with the lugs (corrosion, tightness.etc.).
The neutral is properly bonded to the enclosure. The pipe clamp on the incoming water pipe needs replacement. I'm assuming it is still operational because of the current flow on the ground wire.
The utility did a visual check on the transformer and found everything in order. An engineer also came out and confirmed the problem. He set up instruments for a couple of days. He said it doesn't look like an open neutral at the transformer. The neutal is carrying the unbalanced load from the service equipment.
He told me to check the other buildings as the problem may be elsewhere.
I would appreciate your suggestions how to resolve this matter
It is an apartment building part of a multibuilding complex. It was built in the late sixties, early seventys. The 400 amp, 1 phase, service entrance conductors are in two parallel PVC conduits. They are not properly wired. There are two neutrals and two ungrounded conductors (same phase) in one conduit. There are two ungrounded conductors (same phase), no neutral, in the other conduit.
The conductors land on individual lugs. There is no problem with the lugs (corrosion, tightness.etc.).
The neutral is properly bonded to the enclosure. The pipe clamp on the incoming water pipe needs replacement. I'm assuming it is still operational because of the current flow on the ground wire.
The utility did a visual check on the transformer and found everything in order. An engineer also came out and confirmed the problem. He set up instruments for a couple of days. He said it doesn't look like an open neutral at the transformer. The neutal is carrying the unbalanced load from the service equipment.
He told me to check the other buildings as the problem may be elsewhere.
I would appreciate your suggestions how to resolve this matter