For service equipment (article 250), where the neutral-to-ground bond exists, it's not uncommon to land ground electrode conductors, equipment grounds and grounded (neutral) conductors onto the neutral bus in the switchboard.
However, can you land the grounded (neutral) conductors onto the ground bus, which is electrically connected through the bonding jumper to the neutral bus? I'm thinking "no" due to NEC 110.5 but I'd like to hear others thoughts. Thanks
However, can you land the grounded (neutral) conductors onto the ground bus, which is electrically connected through the bonding jumper to the neutral bus? I'm thinking "no" due to NEC 110.5 but I'd like to hear others thoughts. Thanks