Hey guys,
I have the following 2 questions:
1. I'm sure the answer is yes, but just in case there's a code nuance that i'm unaware of: are you allowed to pull single phase service entrance conductors from a service end box (service end box is the NYC nomenclature for the 'service point') that has 120/208, 3 phase, 4 wire incoming service conductors from the utility? Or are you limited to just pulling 3 phase service entrance conductors from that service point over to your service equipment? I'm reviewing a proposed design that has a mix of 3 phase and 1 phase service entrance conductors tapping from a 3 phase service point.
2. I was at a building today that has a service switch that fed 2 fused disconnect switches downstream. However, I realized as I was writing down my notes that the service switch was unfused. it was an old, old switch (rated 1000 amps), with just the lever and nothing else. I imagine this would still be considered the service switch, even though it's unfused?
I have the following 2 questions:
1. I'm sure the answer is yes, but just in case there's a code nuance that i'm unaware of: are you allowed to pull single phase service entrance conductors from a service end box (service end box is the NYC nomenclature for the 'service point') that has 120/208, 3 phase, 4 wire incoming service conductors from the utility? Or are you limited to just pulling 3 phase service entrance conductors from that service point over to your service equipment? I'm reviewing a proposed design that has a mix of 3 phase and 1 phase service entrance conductors tapping from a 3 phase service point.
2. I was at a building today that has a service switch that fed 2 fused disconnect switches downstream. However, I realized as I was writing down my notes that the service switch was unfused. it was an old, old switch (rated 1000 amps), with just the lever and nothing else. I imagine this would still be considered the service switch, even though it's unfused?