In a separately derived system the service equipment (disconnect) is the transformer disconnect. Why not just call the transformer disconnect a service equipment?
 
Thats good but service and service equipment are two different things with rwo different definitions
 
Unless it's marked service equipment only, we can use it for feeders and sub-panels and such.
 
Unless it's marked service equipment only, we can use it for feeders and sub-panels and such.
Correct.
Suitable for Use as Service Entrance means the neutral and ground bonding is can be added or removed in the field.
Suitable Only as Service Entrance means there is a nonremovable neutral to ground connection from the factory.
 