can a Nema 3R be used as a service equipment? there is a master electrician saying that he used Nema 3R as service equipment

Sent from my CPH1909 using Tapatalk
 
The 3R rating is just the environmental rating. Any type of equipment, including service equipment can be installed in a 3R enclosure.
 
It would have to say on the tag/sticker info the following. “Suitable for use as service equipment” to be used for service equipment.
 