can a Nema 3R be used as a service equipment? there is a master electrician saying that he used Nema 3R as service equipment

Sent from my CPH1909 using Tapatalk
 

don_resqcapt19

Moderator
Staff member
Location
Illinois
Occupation
retired electrician
The 3R rating is just the environmental rating. Any type of equipment, including service equipment can be installed in a 3R enclosure.
 

Dsg319

Senior Member
Location
West Virginia
Occupation
Wv Master “lectrician”
It would have to say on the tag/sticker info the following. “Suitable for use as service equipment” to be used for service equipment.
 