In the following graphic...
Since the temp rise is 40?C, and the service factor is 1.15, then I can use 125% overload protection per 430.32(A)(1).
If the service factor were 1.14 and the temp is 40?C, then I must use no greater than 115%.
If the service factor were 1.15 and the temp is 41?C, then I must use no greater than 115%.
Are all the above observations correct?
Since the temp rise is 40?C, and the service factor is 1.15, then I can use 125% overload protection per 430.32(A)(1).
If the service factor were 1.14 and the temp is 40?C, then I must use no greater than 115%.
If the service factor were 1.15 and the temp is 41?C, then I must use no greater than 115%.
Are all the above observations correct?